Alert When Modbus TCP Device Goes Offline

Jimmy_T
3-Newcomer

Alert When Modbus TCP Device Goes Offline

Is there a way to send out alerts from Kepware whenever a connected Modbus TCP/IP device disconnects?

For example, when these errors are shown:

JT_10361438_0-1676039858447.png

Thank you!

ACCEPTED SOLUTION

Accepted Solutions

You should look into the _Error tag from the _System tag group of the device. 

View solution in original post

2 REPLIES 2

You should look into the _Error tag from the _System tag group of the device. 

Jimmy_T
3-Newcomer
(To:rjanardan)

I like this approach.

We are going to use the Advanced IoT Plugin to scan the "_System._Error" device tags.

If they are true, then there is a disconnection. If they are false, everything is working fine.

 

Thanks!