Fault TAG
Good morning,
I would like to create a tag, mentioned boolen type flip-flop, which the automation will set to 1 and I would like Kepware to automatically and immediately set to 0.
In this way I can alert the automation when communication is missing.
I found a thread that covered a similar, but still unresolved topic:
Solved: Disable tags when PLC is offline and re-activate w... - PTC Community
Thank you.
Solved! Go to Solution.
- Labels:
-
Configuration
-
KEPServerEX
-
OPC
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Notify Moderator
It sounds like you are describing the already built in System tag called _Error and _NoError. The _Error tag is a Boolean tag that gets triggered when the connection to the device is disrupted. Here is a link to the page in help file that covers the use of this tag:
Unfortunately, there is no tag for the server itself. A lot of users use the Server System Tag called _TimeSecond to monitor the uptime of the sever. Here is a link to the page in help file that covers this tag:
Thanks,
*Chris
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Notify Moderator
It sounds like you are describing the already built in System tag called _Error and _NoError. The _Error tag is a Boolean tag that gets triggered when the connection to the device is disrupted. Here is a link to the page in help file that covers the use of this tag:
Unfortunately, there is no tag for the server itself. A lot of users use the Server System Tag called _TimeSecond to monitor the uptime of the sever. Here is a link to the page in help file that covers this tag:
Thanks,
*Chris