Community Tip - Did you get called away in the middle of writing a post? Don't worry you can find your unfinished post later in the Drafts section of your profile page. X
Hello!
I'm configuring a PLC device inside a local network (a S7-1500 with endpoint opc.tcp://192.168.0.190:49320) and already configured a NAT device to translate the local IP for a public IP at the VLAN (10.10.230.235).
From my server I can ping the NAT but when I try to configure it into Kepware (installed at the same server) it doesn't find any available endpoints. I tried also to configure it using "Discovery Server" function.
Any ideas in how to configure a endpoint behind a NAT address?
Thanks in advance!
Solved! Go to Solution.
Kepware has a couple of knowledge base articles that covers the use of NAT devices with Kepware products. Here is a link to the articles which only require a free "My Kepware" account login credentials to access.
Article - CS320299 - NAT devices in PTC Kepware Products
Article - CS307824 - OPC UA Client driver fails to connect to OPC UA server in PTC Kepware Products
As the articles suggest, there will need to be some port forwarding required for the connection to work.
Thanks,
*Chris
Kepware has a couple of knowledge base articles that covers the use of NAT devices with Kepware products. Here is a link to the articles which only require a free "My Kepware" account login credentials to access.
Article - CS320299 - NAT devices in PTC Kepware Products
Article - CS307824 - OPC UA Client driver fails to connect to OPC UA server in PTC Kepware Products
As the articles suggest, there will need to be some port forwarding required for the connection to work.
Thanks,
*Chris
Hi @cmorehead
At the end I didn't arrived to configure the port forwarding, but as the NAT rule says it worked 1:1.
I used the structure like this:
opc.tcp://<NAT CONFIGURED IP>:<ORIGINAL ENDPOINT PORT>
Thanks a lot for you support!