KepServerex is not reconnection once disconnected

  • June 15, 2024
  • 1 reply
  • 1294 views

Kepserex 6.3 is used

I am connecting delta PLC with modbus serial and all communication is proper and working but for some how i disconnected power of plc, of disconnected cable then reconnected cable then kepservex is not connecting the plc again automatically until i reinitialize it, which setting is necessary to connect with plc automatically after some thing like this occur

#Reconnection #ModbusSerial

Best answer by cmorehead

@AIMI 

 

Most of the KEPServerEX drivers have a Timeout setting that can be adjusted to re attempt the connection to the device. This setting cannot be turned off and the maximum amount of time and attempts depends on the drivers used. Here is a screenshot of device properties that shows the timing setting for the Allen Bradley ControlLogix Driver.

 

 

 

Thanks,

*Chris

1 reply

cmorehead13-AquamarineAnswer
13-Aquamarine
June 18, 2024

@AIMI 

 

Most of the KEPServerEX drivers have a Timeout setting that can be adjusted to re attempt the connection to the device. This setting cannot be turned off and the maximum amount of time and attempts depends on the drivers used. Here is a screenshot of device properties that shows the timing setting for the Allen Bradley ControlLogix Driver.

 

 

 