Has anyone tried connecting to the A/B Powermonitor 5000? The Rockwell manual says we can configure RSLinx as a SLC5/03 as it supports PCCC addressing. I tried SLC5/05 in KepwareEX and this didn't work. Neither did the PLC-5 family, Thanks
Solved! Go to Solution.
Did you end up being able to figure this out? Currently attempting to do the same thing.
EDIT: Ended up figuring this out. Utilized the Allen-Bradley ControlLogix Ethernet Driver, and put the device as a MicroLogix 1100. The table for tag addresses is in 1426-um001_-en-p, Power Monitor 5000 User Manual, Appendix A, starting page 219
"The Allen-Bradley ControlLogix Ethernet device driver": https://www.ptc.com/en/store/kepware/drivers/allen-bradley-controllogix-ethernet
It looks like there are two primary ways to communicate with a Powermonitor 5000 device.
Ethernet/IP, and DeviceNet, - We do not have a generic Ethernet/IP driver at this time, or a DeviceNet driver.
A potential work-around would be using our Allen Bradly ControlLogix Unsolicited driver, that can act as a slave to the device. There may be a way to have the device push/write data to the server. You may need to reach out to Rockwell for assistance with additional device configuration. Here is a link to page in the Rockwell documentation that covers some of the set up:
Thanks,
*Chris
I don't see the Allen Bradley Control Logix Unsolicited driver. I have the Manufacturing Suite license under Kepserver 6.10. Is it called something else?
It is called the Allen-Bradley ControlLogix Server Ethernet driver in the channel creation window. Here is link to the product page:
Allen-Bradley ControlLogix Server | Kepware | PTC
Thanks,
*Chris
Did you end up being able to figure this out? Currently attempting to do the same thing.
EDIT: Ended up figuring this out. Utilized the Allen-Bradley ControlLogix Ethernet Driver, and put the device as a MicroLogix 1100. The table for tag addresses is in 1426-um001_-en-p, Power Monitor 5000 User Manual, Appendix A, starting page 219
Hi Karson, I gave up and reverted to RSLinx, but your solution gives me hope.... and yes, once I worked out how to convert from Symbolic Addressing it looks great. Thanks much for the follow-up.