Hello,
I'm attempting to add a AutmationDirect CLICK PLC
to our Kepware environment, but not seeing this option for the Automation Direct drivers
Anyone ever configure one of these before?
Thanks in advance
Solved! Go to Solution.
Hello, Thank you for contacting us.
It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:
In Kepware,
Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502
Hello, Thank you for contacting us.
It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:
In Kepware,
Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502
Awesome, thanks for this info