Trying to add AutomationDirect CLICK C0-11DD2E-D PLC

GC_10725709
3-Newcomer

Trying to add AutomationDirect CLICK C0-11DD2E-D PLC

Hello,

I'm attempting to add a AutmationDirect CLICK PLC

to our Kepware environment, but not seeing this option for the Automation Direct drivers

 

Anyone ever configure one of these before?

 

Thanks in advance

ACCEPTED SOLUTION

Accepted Solutions

Hello, Thank you for contacting us.

It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:

rajskumar_1-1738846893997.png

 


In Kepware, 

  • Right click on Connectivity and Add New Channel of Modbus TCP/IP Ethernet and change name as per requirement
  • Right click on Channel and Add New Device and change name and IP as per requirement(Modbus default port is 502 but you can confirm with device vendor)
    • Refer this article for ID details in Kepware
  • Add tags based on how it is defined in device
    • Refer driver manual for Modbus Addressing here  
    •  
      rajskumar_4-1738846955361.png

       

       

       

       

Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
 
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502

View solution in original post

2 REPLIES 2

Hello, Thank you for contacting us.

It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:

rajskumar_1-1738846893997.png

 


In Kepware, 

  • Right click on Connectivity and Add New Channel of Modbus TCP/IP Ethernet and change name as per requirement
  • Right click on Channel and Add New Device and change name and IP as per requirement(Modbus default port is 502 but you can confirm with device vendor)
    • Refer this article for ID details in Kepware
  • Add tags based on how it is defined in device
    • Refer driver manual for Modbus Addressing here  
    •  
      rajskumar_4-1738846955361.png

       

       

       

       

Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
 
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502

Awesome, thanks for this info