Community Tip - If community subscription notifications are filling up your inbox you can set up a daily digest and get all your notifications in a single email. X
We have two OPC UA Clients (PC) and want to communicate between them using KepServerEx.
There i no PLC involved!!!
Is this possible?
if it is, which driver should I use?
The clients are Pi System and a customer specific program.
Solved! Go to Solution.
Greetings, you will want to use the Memory driver. It can be configured to persists values on server shutdown but more importantly because it is memory based and does not use a PLC all communications is processed via local memory cache.
Greetings, you will want to use the Memory driver. It can be configured to persists values on server shutdown but more importantly because it is memory based and does not use a PLC all communications is processed via local memory cache.
Worked like a charm!
I have succeeded using the ODBC Client driver and MS SQL Express server (which was what the Swedish distributor recommended...), but this is much simpler!
Thank you very much!
// Anders