Re: How to figure out at which memory address each data from the sensors is being stored in?

SigmaTile

 

Hi Boris,

the adresses are defined in hexadecimal format in the phyton script. Search please for the corresponding variables

You will find 0x1c for the VibrationAlert

0x1C = 28 (from hexa to dec)

add one because of modbus so you get 29

In Modbus the registers 40001-49999 are typically used for analog output holding

So it looks like 40029 for the VibrationAlert.

You can apply the same mechanism for all the other variables / sensor values

Hope it helps you