Tags Write Delay in between KepwareEx to Mitsubishi iQ-R32 PLC
I am using KepwareEx6.15 with Mitsubishi iQ-R32 PLC + RJ71EN71 module.
Kepware Channel and Device configuration point out to the RJ71EN71 module (SLMP TCP/IP port)
I have created SLMP TCP/IP 40 ports for connecting the same PLC+RJ71EN71 module with KepwareEx6.15 multiple channel and devices for limit the tags in each devices for quick poll.
I have active client connections with KepwareEx is 120 and Active tags more than 3000 with scan rate 100ms. I am facing the challenge to write back 200tags values from kepwareEx to PLC it took more than 40 secs.
the below information were my testing observations.
Scenario 1: When i restart the Kepware and disconnect the active client connections and maintain one channel & device with 200 tags the write back time is 6secs.
Scenario 2: When i restart the Kepware and loaded the active clients connections and maintain the one channel and device with 4000 tags and write back time of 200 tags is 60secs
Scenario 3: When i restart the Kepware and loaded the active clients connections and maintain the multiple channel and device with 4000 tags and write back time of 200 tags is 40secs - 60secs(random time observing)
all the above testing duty cycle maintained as 2
scan rate of write back 200 tags as 20ms
Scan mode first time all three scenario respect tag based
Scan mode second time all three scenario respect client specified
Note: When i am increase the tags in Kepware and i felt the performance of KepwareEx i.e write back the values time get increased.
I want to achieve the write back 200 or 300 tags within 2 to 4 secs.
I am expecting a solution in this forum hope anyone face this issue or have any ideas please suggest me.
