Hi, my name is Ben Lau, the Project Engineer from a System Integrator in Hong Kong. I would like to communicate with the Johnson Controls NAE and Schneider SmartX controllers through BACnet I/P driver of your KEPSeverEX software. However, I have difficulties in configuration details:
Installed KEPServer Version: V6.14.263.0 (Demo Version)
Operating System Version: Microsoft Windows 10 Home 64-bit
@LS_10774172
It sounds like the device does not support segmentation. You can verify this by checking the device's PICS statement. If it does not, you can set Device > Properties > Protocol Settings > Max. Items per Request to 1 instead of 16.
Please take a look at the knowledge base article in the following link to help resolve the Error 31 issue:
Article - CS336438 - BACnet error code 31 in PTC Kepware products
Thanks,
*Chris
Hi Chris, thanks for your reply! Let me describe more details on our current job background. Two existing sites have been installed with Johnson Controls NAE and Schneider SmartX controllers respectively for Building Services equipment monitoring and control through BACnet protocol. One workstation in each site is installed with their own brand SCADA software through BACnet I/P. In this case, without interrupting the existing operation, our missions are to:
As mentioned in problems #3 and #4 in previous post, I am not familiar with BACnet I/P configuration details. I wonder what the differences between local device instance (channel protocol setting) and ID (device general setting) are. Take Johnson Controls as an example. Three device levels, each has its own network address / instance number, are found: FC under NAE (controller), DDC (Remote I/O) and Field equipment. The screenshots are attached for your information. Please advise which is which. Thanks!