I have a situation that I am trying to understand to see if this actually can be done. I have a FactoryTalk View application with a Numeric input that is scaled from -0.5 to 0.5 but it is writing directly to the Kepware Tag and is linked to a Modicon Register. I am not scaling the -0.5 to 0.5 in the hmi, I would like Kepware to perform that. So Ftalk input would be -0.5 to 0.5 and then Kepware would scale the -0.5 to 0.5 to 0 - 4095 and write 0 - 4095 to the Modicon PLC. Can this be done?
Solved! Go to Solution.
Hi,
Yes, this absolutely can be done in Kepware — and it's the right way to do it when you want to keep your HMI logic clean and offload the scaling to the OPC layer.
Kepware has a feature called Linear Scaling built into its Tag Configuration, which allows you to scale the raw PLC values (in your case 0–4095
) to engineering values (e.g., -0.5 to 0.5
and vice versa.
Here's how you can set it up:
Browse or manually add the tag pointing to the correct Modicon register (e.g., 400001
or %MW1
, etc.).
In the tag configuration:
Right-click the tag → Properties → Select the Scaling tab.
Check Enable Linear Scaling.
Scaled (Engineering) Range:
Low: -0.5
High: 0.5
Raw (Device) Range:
Low: 0
High: 4095
Verify that Scaling applies to both read and write operations.
This ensures that when FactoryTalk writes -0.5
, Kepware scales and sends 0
to PLC.
When PLC returns 2048
Kepware scales it back to 0.0
for FactoryTalk.
Ensure your Numeric Input object in FactoryTalk is bound to this OPC tag.
FactoryTalk will see only -0.5 to 0.5
, unaware of the underlying 12-bit raw range.
Ensure the tag datatype is INT
or WORD
(Modicon register type) that can handle 0–4095
properly.
Double-check that Modicon doesn’t expect any special format (e.g., signed, BCD).
If writing fails or scales incorrectly, try adjusting the tag’s data format (e.g., Unsigned Word vs Signed Word).
Thanks,
Hi,
Yes, this absolutely can be done in Kepware — and it's the right way to do it when you want to keep your HMI logic clean and offload the scaling to the OPC layer.
Kepware has a feature called Linear Scaling built into its Tag Configuration, which allows you to scale the raw PLC values (in your case 0–4095
) to engineering values (e.g., -0.5 to 0.5
and vice versa.
Here's how you can set it up:
Browse or manually add the tag pointing to the correct Modicon register (e.g., 400001
or %MW1
, etc.).
In the tag configuration:
Right-click the tag → Properties → Select the Scaling tab.
Check Enable Linear Scaling.
Scaled (Engineering) Range:
Low: -0.5
High: 0.5
Raw (Device) Range:
Low: 0
High: 4095
Verify that Scaling applies to both read and write operations.
This ensures that when FactoryTalk writes -0.5
, Kepware scales and sends 0
to PLC.
When PLC returns 2048
Kepware scales it back to 0.0
for FactoryTalk.
Ensure your Numeric Input object in FactoryTalk is bound to this OPC tag.
FactoryTalk will see only -0.5 to 0.5
, unaware of the underlying 12-bit raw range.
Ensure the tag datatype is INT
or WORD
(Modicon register type) that can handle 0–4095
properly.
Double-check that Modicon doesn’t expect any special format (e.g., signed, BCD).
If writing fails or scales incorrectly, try adjusting the tag’s data format (e.g., Unsigned Word vs Signed Word).