Hello Developers,
We are facing some problems trying to connect the Siemens power monitoring device "PAC3200" with KEPserverEX 6.5, using the Modbus TCP/IP protocol, the basic configuration are done using its manuals (attached) but we still have a Bad Quality in the tags.
This is basic configuration for the device:
For the tag:
Just a tag example from the PAC manual:
This is a variable that we can use the function code 0x03 and 0x04 (page 40).
I tried to use the address 400001, 30001, 300001, disable the zero-based-addressing, modbus-byte-order and nothing works.
Note: I can ping the device with no issues.
Kind Regards.
Solved! Go to Solution.
Hello Claudio,
This device probably has a station/node/slave address assigned to it. For example the SquareD power meters have a default station address of 7 so you would use this in place of the default '0' in the Device ID, making it "<172.17.31.156>.7" .
The Siemens configuration software should indicate in some way what that station/node/slave ID is.
Best Regards,
KC
Hello Claudio,
This device probably has a station/node/slave address assigned to it. For example the SquareD power meters have a default station address of 7 so you would use this in place of the default '0' in the Device ID, making it "<172.17.31.156>.7" .
The Siemens configuration software should indicate in some way what that station/node/slave ID is.
Best Regards,
KC
Hello Mr. KCorrigan,
You were totally right!!
It's working now! The ID 7 was the right ID.
Thank you very much for your support!