KEPServerEX OPC UA Client Driver Unable to Connect to CIMON OPC UA Server
uvcssb
1. Current Situation
CIMON OPC UA Server Information:
  • IP: [CIMON OPC UA Server IP]
  • Port: [CIMON OPC UA Server Port]
  • Network: Same local network (Ping test and TCP connection successfully confirmed).
KEPServerEX Status:
  • The OPC UA Client Driver in KEPServerEX cannot detect the CIMON OPC UA Server during server discovery.
  • Even when the Endpoint URL is manually entered, the connection fails.
Other Client Status:
  • UaExpert:
    • Successfully connects to opc.tcp://[CIMON OPC UA Server IP]:[CIMON OPC UA Server Port] (with Security Policy: None, Message Security Mode: None).
    • Node browsing and data reading from the CIMON OPC UA server work perfectly.
  • Node.js (node-opcua library):
    • Successfully connects to the same Endpoint URL and reads data successfully (with Security Policy: None, Message Security Mode: None).
2. Troubleshooting Attempts
Network Connection Check:
  • From the machine running KEPServerEX ([KEPServerEX Machine IP]):
    • Ping to [CIMON OPC UA Server IP] → Successful response.
    • Test-NetConnection [CIMON OPC UA Server IP] -Port [CIMON OPC UA Server Port] → TCP response successful.
  • No network connection issues detected between KEPServerEX and CIMON OPC UA Server.
Firewall Configuration:
  • Allowed TCP Port [CIMON OPC UA Server Port] on the machine running KEPServerEX ([KEPServerEX Machine IP]).
  • Configured both inbound and outbound rules.
Security and Authentication:
  • Configured KEPServerEX with Security Policy: None and Message Security Mode: None to match the CIMON OPC UA Server.
3. Main Issue
The issue does not appear to be related to network connectivity or security/authentication configurations.
While other clients (UaExpert, Node.js-based clients) successfully connect to the CIMON OPC UA Server, only KEPServerEX fails to discover or connect to the server.
4. Environment Details
  • KEPServerEX Version: v6.17.240.0
  • Machine Running KEPServerEX:
    • IP: [KEPServerEX Machine IP]
  • CIMON OPC UA Server:
    • Security Settings: Security Policy None, Message Security Mode None
  • Network Environment: Same local network, TCP Port [CIMON OPC UA Server Port] allowed through the firewall.
rajskumar
(To:uvcssb)
Hello, Thank you for the detailed description.
Are you encountering any errors while browsing the CIMON OPC UA Server (in manual connection)? Please verify the client-side configuration using the article below.
https://www.ptc.com/en/support/article/CS298913
If you are prompted to log in to view the complete article, you can use your MyKepware login credentials.
Additionally, I suggest capturing Wireshark packets to identify the issue.
uvcssb
(To:rajskumar)
Current Situation
  1. CIMON OPC UA Server Details
    • IP: [CIMON_IP]
    • Port: 4840
    • Security Policy: None
    • Message Security Mode: None
  2. UaExpert Connection
    • Successfully connects to the CIMON OPC UA Server, allowing node browsing and data reading.
  3. Node.js Connection
    • Successfully connects to the CIMON OPC UA Server, enabling data read/write operations.
  4. KEPServerEX Connection
    • Using the OPC UA Client Driver, attempting to connect to the CIMON OPC UA Server results in a BadTcpMessageTooLarge error.
    • Wireshark packet analysis shows that after sending a GetEndpointsRequest, the CIMON OPC UA Server returns this error.
Wireshark Request Packet Comparison
  1. UaExpert Request Packet:
    • Message Size: 98 bytes
    • Details:
      • EndpointUrl: opc.tcp://[CIMON_IP]:4840
      • LocaleIds: None (ArraySize: 0)
      • ProfileUris: None (ArraySize: 0)
  2. KEPServerEX Request Packet:
  3. TCP Segments Comparison:
    • UaExpert Request: Sent in a single TCP segment.
    • KEPServerEX Request:
      • Reassembled TCP Segments:
        • Frame #101: 12 bytes
        • Frame #102: 4 bytes
        • Frame #103: 151 bytes
      • Total Length: 167 bytes
    • It seems the CIMON OPC UA Server might have trouble handling segmented TCP packets from KEPServerEX.
  4. Comparison Results:
    • KEPServerEX’s request is slightly larger due to the inclusion of ProfileUris.
    • However, 167 bytes is not typically considered a "large message" in OPC UA communications.
    • UaExpert successfully handles requests larger than 167 bytes without issues.
Steps Taken to Resolve
  1. Network Connection
    • Ping and TCP connection tests confirm accessibility (Port 4840).
  2. KEPServerEX Configuration
    • Configured with Security Policy: None, Message Security Mode: None.
  3. Wireshark Analysis
    • Compared request message size and TCP segments between UaExpert and KEPServerEX.
    • KEPServerEX’s request is sent in multiple TCP segments, which might not be properly handled by the CIMON OPC UA Server.
uvcssb
(To:rajskumar)
Current Situation
  • IP: [CIMON_IP]
  • Port: 4840
UaExpert Connection
Node.js Connection
  • Details:
Comparison Results
Network Connection
Wireshark Analysis