Hi,
I have the similar problem as NM_12850686. Could you please share the port issue solution?
Here is my setup:
Cleco Controller mPro200 - Open Protocol - Port 9002 - Activated
Cleco Controller mPro200 - TorqueNet- Port 12345 - Activated
Cleco Controller mPro200 id : 192.168.50.20
KepServerEx - Channel:TorqueToolEthernet - Device:Cleco (Open Protocol - 192.168.50.20 - Port: 9002)
Both the controller and the port can be ping successfully from the PC.
However, none of the tags receives information from Cleco. Could you please look into this?
Thank you,
LP
Hi @LP_12507955
My Observations are
Your Test-NetConnection
result shows port 9002 is reachable.
Device IP is correct.
Controller port is activated, and protocol is set to Open Protocol.
No MID 001 Communication happening
From your Kepware logs and screenshots:
Kepware is not receiving responses from Cleco (timeouts or blank reads).
Likely causes:
Incorrect MID polling config
Missing handshake
Wrong Job selection, or missing Start request MID
Cleco not configured to auto-transmit data
Solutions May be:
1. Controller-Side Validation
On the Cleco mPro200, go to:
Menu > Protocol Settings > Open Protocol > Advanced
Ensure MID 001, 005, 006, 0062, 0064 are activated for replies
Set Primary Trace MID = 0064
or the expected MID your system should respond with
Enable Auto-send MID 0064 on job completion
Also check:
"Controller Auto Start Job" is enabled
Job ID is pre-assigned or ready to be started from OPC (Kepware)
Why this matters: If the controller is waiting for a MID 003 (Job Select) or MID 001 handshake, and it's not received, it won't push out MID 0064 (tightening results).
2. Kepware Device Settings
From your screenshot:
Job Select Method: Try setting it to None
initially for testing
Start MID: Enable “Send MID 003” to select Job
Enable Auto-send MID 0064 (result transmission from Cleco to Kepware)
Also:
Increase Timeout from 5000 ms to 10000 ms for slow reply testing
Ensure Device Read Mode is set to either On Demand or Cyclic (not “None”)
3. Trigger Initial MID
Kepware won’t automatically initiate MID 001 unless the driver does so or tags are manually activated.
To verify:
Go to Quick Client
Right-click any writable command tag (like MID_003_JobNumber
) and write a valid job number
Then write 1
to the Send_Job
tag (or equivalent) to send MID 003
Observe if Cleco replies with MID 006 or MID 0064
If this works, the issue is that the controller needs an explicit MID trigger to start sending.
Use UaExpert to Compare
If the MES is not reading but UaExpert is:
Use UaExpert to create a monitored item on tag like Torque
or ResultID
Perform a real tightening operation on Cleco
See if MID 0064 values populate
If UaExpert sees values but Kepware does not:
Likely a job trigger/start MID missing from Kepware
Or MES needs to send command MID to initiate data
5. Firmware or Protocol Mismatch
Check:
Cleco firmware matches the Open Protocol version expected by Kepware
If Cleco uses a custom MID map, the default OPC tag structure in Kepware may not match
Use Cleco’s documentation to verify which MIDs are enabled and what data formats are used.
Thanks,
Things I learned - you can't read tool_enable only write it.
You need to add every tool in kepserver.
They will have the same IP address as the controller but the port that is mapped to them in the controller.
You will need to address the tool as toolname.tagname when controlling remotely. I used ignition and OPC
Easiest thing to get working is reading the CommChanelId - should match the toolgrp in the cleco controller.
Also you can send TimeSync and read back time.
If you get those working through quick client, you're good.
I found Cleco MPRO was best controlled via app numbers. I am using no MIDs directly.
I am sending enables, app numbers, and reading back LTRs. All those are available in the tag library when you add a new tag.
I mostly got tripped up on needing to use app numbers and on needing to use the tag library in KepServer. When I tried to use MIDs to start communication for example, that was built into kepserver. If you let the tool do the work, it is easier.