Hello,

 

I have one device that uses the Modbus protocol. and Thingworx Kepware server connects that Modbus device and sends data to thingworx. And I have displayed device data in a mashup. In that mashup, I have added an on/off button. when I press the off button on mashup then my device will off 

 

How can I achieve this using Thingworx, and the Thingworx Kepware server? 

 

1 ACCEPTED SOLUTION

Accepted Solutions

Hi @ParthBhadiyadra 

 

Do you have a register in PLC to control power ON / OFF?

 

If the register is available, you can bind that register to Kepware Tag and Thingworx Property. By updating the property value from Thingworx you can control the PLC power state.

 

Make sure the register is Readable / also Writeable 

 

/VR

View solution in original post

2 REPLIES 2

Hi @ParthBhadiyadra 

 

Do you have a register in PLC to control power ON / OFF?

 

If the register is available, you can bind that register to Kepware Tag and Thingworx Property. By updating the property value from Thingworx you can control the PLC power state.

 

Make sure the register is Readable / also Writeable 

 

/VR

Thank you so much @Velkumar 