After upgrading from ThingWorx 9.1 to 9.2.6-b366 the 'Automatically update values when able' only works for administrators.
When opening a mashup with as a non-admin user the application log states:
- Not authorized for ServiceInvoke on ForwardEvent in PersistentSession
- Unable to Invoke Service AddDynamicRemoteSubscription
We verified Article CS346816 - https://www.ptc.com/en/support/article/CS346816 but didn't solve our problem/
Is there any change within 9.2.6 we need to consider?
Hi @Rutger.
From a review of the case that was opened, I see that adding the Visibility permission on EntityServices resolved the issue. Please let us know if you agree.
--Sharon
Based on the error you need more permissions than the ones in the article.
I would add those ServiceInvoke calls as Runtime Execute overrides for your users.
Thank you for your reply.
Can you give me some guidance? Where should I change this? At Mashup or Thing?
I usually just look at the script/application log, because it will call out the Thing/Resource/Subsystem and the Service being invoked.
Or use the Developer tools, and check the lines in red.
Then I will go and set security on that entity and add an Override for that specific service to allow execution.
I'll basically repeat that until all the errors are gone.
Hi @Rutger.
--Sharon
Hi @slangley ,
Indeed, adding the Visibility permission on EntityServices resolved te issue.
Thanks for the follow up.
Kind regards,
Rutger