Connection path through CompactLogix in Dual-IP Mode

JordanCClark
2-Guest

Connection path through CompactLogix in Dual-IP Mode

Trying to connect to an L30ER through an L310ER in Dual IP Mode. KEPServerEX Version is 6.10

JC_10620513_0-1678742659080.png

As close as I can tell, the ID should be:

<10.10.10.1>,1,[4,192.168.1.2,1],0

However, I get an Invalid Device ID

 

I can connect through Ignition's OPC server with a connection path of. 4,192.168.1.2,1,0, but I'm not sure how that translates to KEPServer's ID.

 

ACCEPTED SOLUTION

Accepted Solutions

This is not possible within the driver at this time. Please refer to this article where that functionality is mentioned under the "Limitations" section.

 

https://www.ptc.com/en/support/article/cs299190

 

Best regards,

Andy Servetas
Principal Technical Support Engineer | Kepware Technologies

 

 

View solution in original post

3 REPLIES 3

This is not possible within the driver at this time. Please refer to this article where that functionality is mentioned under the "Limitations" section.

 

https://www.ptc.com/en/support/article/cs299190

 

Best regards,

Andy Servetas
Principal Technical Support Engineer | Kepware Technologies

 

 

Thanks, Andy. Do you happen to know if there's anything on the roadmap for this?

I have not heard of it being added to the product roadmap yet.

 

-Andy