Does anyone have experience with connecting to Proface HMI GP4000 series?
Which driver should I select?
Solved! Go to Solution.
An HMI is typically a client connection into KEPServerEX and no driver would be required to make that OPC UA or OPC DA connection. You would need to the Kepware OPC UA or DA Client driver if the Proface HMI GP4000 is acting as an OPC server where KEPServerEX would be acting as the client.
Thanks,
*Chris
An HMI is typically a client connection into KEPServerEX and no driver would be required to make that OPC UA or OPC DA connection. You would need to the Kepware OPC UA or DA Client driver if the Proface HMI GP4000 is acting as an OPC server where KEPServerEX would be acting as the client.