Solved

Could not communicate to Allen Bradley Controllogix over Satellite Communication

  • August 11, 2024
  • 1 reply
  • 961 views

I have upgraded KepServerEx.V5 to V.6. It can communicate with ControlLogix before upgrading. After upgrading to V.6. 

Best answer by rajskumar
  • The latest Kepware versions have not undergone testing with the older firmware of Allen Bradley PLC
    • Here is the tested firmware versions as per Allen-Bradley ControlLogix Ethernet driver manual
  • While switching the Protocol Mode to Symbolic has been successful in some cases, it does not provide a guaranteed solution
    • Right click on the device in the channel
    • Select Properties
    • Select Logix Options
    • Under Protocol Options change Protocol Mode to Symbolic 

1 reply

rajskumar16-PearlAnswer
16-Pearl
August 12, 2024
  • The latest Kepware versions have not undergone testing with the older firmware of Allen Bradley PLC
    • Here is the tested firmware versions as per Allen-Bradley ControlLogix Ethernet driver manual
  • While switching the Protocol Mode to Symbolic has been successful in some cases, it does not provide a guaranteed solution
    • Right click on the device in the channel
    • Select Properties
    • Select Logix Options
    • Under Protocol Options change Protocol Mode to Symbolic