Could not communicate to Allen Bradley Controllogix over Satellite Communication

PA_8832783
3-Newcomer

Could not communicate to Allen Bradley Controllogix over Satellite Communication

I have upgraded KepServerEx.V5 to V.6. It can communicate with ControlLogix before upgrading. After upgrading to V.6. 

ACCEPTED SOLUTION

Accepted Solutions
rajskumar
15-Moonstone
(To:PA_8832783)

  • The latest Kepware versions have not undergone testing with the older firmware of Allen Bradley PLC
    • Here is the tested firmware versions as per Allen-Bradley ControlLogix Ethernet driver manual
  • While switching the Protocol Mode to Symbolic has been successful in some cases, it does not provide a guaranteed solution
    • Right click on the device in the channel
    • Select Properties
    • Select Logix Options
    • Under Protocol Options change Protocol Mode to Symbolic 

View solution in original post

1 REPLY 1
rajskumar
15-Moonstone
(To:PA_8832783)

  • The latest Kepware versions have not undergone testing with the older firmware of Allen Bradley PLC
    • Here is the tested firmware versions as per Allen-Bradley ControlLogix Ethernet driver manual
  • While switching the Protocol Mode to Symbolic has been successful in some cases, it does not provide a guaranteed solution
    • Right click on the device in the channel
    • Select Properties
    • Select Logix Options
    • Under Protocol Options change Protocol Mode to Symbolic 