Algorithm to Calculate Soil Wedge Area, Weight, and Centroid Behind a Retaining Wall
Eng_ReyD_497
This is a clarified follow-up to a previously solved question. The new objective is to compute the soil wedge area, weight, and centroid (CGx, CGy) behind a retaining wall using the mathematical approach described in the attached Mathcad files, and input data is already explained in the attachment. I am using Mathcad Prime 11. Any help would be appreciated.
(To:Werner_E)
According to your explanations in the PM you sent to me
"To clarify, in addition to the soil self-weight, these loads represent surcharge (live) loads such as pedestrian or vehicular loads, etc.."
and
"If the surcharge region overlaps the critical wedge, only the overlapping length is considered."
I understand why only the second load can have any effect and so the others must result in zero.
I added violet boxes to represent the position of those loads and it can clearly be seen that load1 is to far to the left to be able to affect the wedges and load3 it too far to the right as beta is not lower than 34°. We would need an angle ß of 23° or lower to have xb exceed the 37,5 ft and so make load3 to have an effect.
The pic shows the situation with ß being the lowest value of interest (34°) and your function lsurLL correctly returns that the wedge is overlapped by load2 for its full length of 12 ft.
EDIT: I removed the point-in-polygon test area because that function is not used at all.
Also removed the calculation of 'weight' in the 'calculate' function as it easily can be calculated outside.
The "Intersect" function was taken from an older sheet of mine where points were represented by complex numbers (real part = x-coordinate, imag. part = y-coordinate) and polygons by simple vectors of complex numbers.
The functions for calculating area and center of gravity of a polygon assume polygons to be  presented as a nx2 matrix of real numbers.
replaced attached sheet
16 REPLIES 16
Here is something I used to use to find the log spiral failure surface behind the wall for the active and passive horizontal and vertical pressures.
Cheers
Terry
Thanks @terryhendicott ,
I very much appreciate sharing your solutions, which shows that you are familiar with the problem I need to resolve. The example you shared is still does not give what I would need, and I do not know how to tweak it!! My MathCAD skills are still not as good as you may think!
I will need to calculate the area(s) and centroid(s) (CGx, CGy) of each shape bounded by the vertical plane and the inclined planes bounded by the dashed lines incrementally. The challenges to do this is to identify the coordinates of the intersecting points with the soil, then calculate the area(s), whether they are triangles or polygon, and their centroids (x & y) for each shape and so on.
This is the "trial wedge method". I appreciate sharing your problem, but I am not sure how to tailor it to get it to do the trial wedge.
For a given angle ß (running from 90° down to 34°), which polygon are you looking for to calculate area and centroid?
The left or the right in this picture:
Is there a guarantee that the first segment in xy has an intersection with the vertical line at B1?
This means that the second x-value in xy is always larger than B1.
EDIT: Your reply to Terry seems to make clear that you have the left version in mind where the vertical line at B1 is a border.
The last question is not that important as we can run through xy until we come across a point to the right of B1,
P.S.: I think it was a mistake that you marked this post as the correct answer. You should remove that mark as others may ignore a thread they think is already answered.
Thanks @werner ...
1) The left.
2) I am not clear on the second question, regarding intersection with B1, but I will answer both scenarios I thought you might mean
a) If I assume that you mean the vertical line, which is referenced as "Pressure plane", this is where the first segment starts, so the vertical line is one side of the segment. The intersection I mean will be with the soil profile which is the topmost line.
b) If you mean β₁ instead (the angle), what I am showing is read as βᵢ "with subscript letter i not 1"
as the iteration progresses, the wedge continuously increases in size, as you show on the left, and each new wedge has its own updated centroid.
The angle βᵢ is not intended to represent a single fixed plane, as I shown (I apologize!). Rather, it is a dynamic parameter representing each incremental dashed plane (β₁, β₂, β₃, β₄, and so on).
The dashed lines I am showing at these locations are just schematic for illustration purposes only. In practice, the dashed planes represent approximately 1,000 individual planes, each associated with a unique corresponding β angle value, starting from the vertical line (pressure plane), and rotating until it with the solid green line. I understand it was confusing,
As shown in my file, the angle β is generated using an equation that computes about 1,000 incremental angles ranging from 90° to 34°, with each step equal to 1/1000 of the total angular range.
I realize the dashed lines I added, for illustration, may have caused some confusion, my apologies!. The blue solid line shown happens to align with one of the planes in my model, but the dashed planes are not fixed at those locations. They are virtual and schematic only, generated dynamically during the iteration process.
I’ve also added a couple of notes to the original sketch for clarity. (attached). Please let me know if this addresses your questions, and I truly appreciate your help.
What I meant with my second question was if the soil polygon could also look that way:
Here the vertical line at x=B which is the left border of the polygon of interest does not intersect the first segment of the soil polygon.
But it doesn't matter anymore. The solution I am about to post should be able to deal with this situation as well.
The 1st polygon is any area bounded by the vertical line at x=B, the dashed line" first calculated dashed line, not necessarily the shown", and the soil portion in between both lines
The 2nd polygon is the area bounded by the vertical line at x=B, the "second" dashed line, and the soil portion in between both lines, the vertical and the second dashed line), and so on with the third and forth and so on until completing the iterations
What I mean by polygon is the shape, whether it is a triangle or polygon ... I use term polygon as a generic name to the shape...
The yellow shade does not represent something specific; it represents a wedge getting larger as we progress
Yes, I guess I got it. See the solution in my answer below.
OK, based on the informations so far here is my attempt.
I provide a function "calculate" which, given the angle beta and the soil polygon as input returns area, center of gravity, weight and also the polygon so we can plot it. Its not completely self-contained as it relies on variables B1 and gamma to be defined in the worksheet.
Of course this function "calculate" can also be used to create a table of values. I have chosen 1120 steps because this will make for a nice step value of 0.05 degree but of course that value can be freely chosen.
Because Prime does not allow to change the units in a matrix with mixed units i decided to create a table with dimensionless values and add a header line which specifies the units.
Hope this helps
Prime 11 sheet attached
(To:Werner_E)
Found an error in the sheet (it would not deal correctly with more weird soil polygons).
Fixed version attached
(To:Werner_E)
Damned!
Fixing the previous problem introduced a new bug which lets the calculation fail for the pathologic case of  ß=90°.
Is fixed in the attached file!
This is excellent high-level code! Thank you @Werner_E very much for taking the time to put it together.
If possible, I’d appreciate your help with a few additional refinements to the results matrix (“table”) so I can fully use it for my application (notes are highlighted in the attached file as well):
1- Compute hd1, as indicated near the beginning of the worksheet.
2- Add xᵦᵢ, the x-coordinate of the intersection between the rotating surfaces (the green dashed lines) and the ground profile.
3- Add Wₛᵤᵣs1, Wₛᵤᵣs2, and Wₛᵤᵣs3, parameters, calculations and functions I prepared are already provided; I just need the results included as table columns.
4- Add Pwi, defined as the sum of several of the above quantities. (explained in the attached file)
Once included, I’d like to extract the governing values from the final table, specifically the maximum Pw and the corresponding β and xᵦ.
I highlighted all the above in the attached file. I appreciate your great help and jumping into this.
Thanks again for your time and help, I really appreciate it. Please let me know if anything is not clear
Here is the modified worksheet.
I also added a way to create single vectors for all the desired quantities instead of a compact table as it seems that's what you actually are looking for.
You may have to check the logic in your function  lsurLL  because this function returns 0 feet for any value xb provided - at least when used with LL index 1 and 3. Or is this intentional?
Always check your functions by evaluating them using some test data!
You may also test them with a vector of sample values if you use vectorization:
(To:Werner_E)
and
Thanks @Werner_E   this is really brilliant! Much appreciated.
It appears to be working perfectly and fully resolves my original question. Thank you again for the excellent solution. I do have a couple of follow-up questions as I’m still learning from this, if you don’t mind:
1. At the bottom of the attached file, I tried calculating the soil area/volume using an alternative method (by integration) that I previously learned from you in an earlier post. It produced the same results, which is reassuring. I added it on the side page (7). I appreciate if you can explain the difference between the two approaches, specifically, since the older methods appears to be simpler form of the solution you provided in this question, or whether it has limitations compared to it.
2. If it’s straightforward for you, and ONLY if you have time, I was wondering about a possible extension purely for learning purposes. Specifically, how this approach might be adapted for multiple blocks, where the calculation is performed independently for each course using a vertical reference line at X=B1, X=B2, X=B3, etc. depends on the level we are exploring (see the attached second file).
I understand both points are beyond the original scope, which was complicated problem already to describe! I completely understand if you’d prefer not to go further. I’m also happy to post this as a separate question if you feel that’s more appropriate. Either way, I will consider your current answer a complete and final solution regardless. Thanks Again
I vaguely remembered your previous question but i did not search for it to look it up. So this time I concentrated on the polygon approach and used Gauß* "shoelace" method to calculate the area and a related method to calculate the center of gravity.
At first glance i see no benefit in the one or the other method and guess you could use whatever you feel more comfortable with.
Double integrals may take more time to calculate and may yield some nasty round-off errors because of the numerical integration algorithm used, but I guess that this does not make that much difference in your case.
BTW, you could use tan(ß) instead of defining psi:=90°-ß  and then cot(psi)
Remark: The method as you had used it fails for ß=90° (when the polygon degenerates to a line segment with area zero.
I opened your "multi blocks" file but found no drawing of what you actually try to achieve. So I don't see what the postion of any additional blocks would be, which polygons you would like to observe, etc.
It seems to me that this question would justify a new thread and more detailed expanantions.
Perfect, @Werner_E   yes, that was a previous question I asked about six months ago. The earlier post included a more representative sketch, but at the time I wasn’t able to clearly articulate this specific extension.
Thank you very much again for the detailed explanation and helpful remarks. I’ll organize my thoughts and supporting figures and post this as a new question in the next day or two. Best regards!
