hi guys,
Could you know whether Kepware Server can support communication between Siemens PLC and Siemens Desigo CC via BACnet/IP?
Although Siemens provides a BACnet gateway for BACnet integration, its network configuration does not comply with IT security requirements. Therefore, I would like to know if Kepware can perform protocol translation. If so, could you provide a configuration manual?
Thank you very much.
pshashipreetham
Yes, Kepware (KEPServerEX) can be used to communicate between a Siemens PLC and a Siemens Desigo CC system using BACnet/IP by acting as a protocol gateway.
Here’s how it can be set up:
  1. Use the Siemens Ethernet Driver in KEPServerEX to connect to the Siemens PLC (S7-1200, S7-1500, S7-300, etc.).
    • Configure the PLC connection using the proper rack/slot and IP address.
    • Verify data access by browsing the PLC Tags in the Kepware client (Quick Client).
  2. Enable the BACnet/IP Driver in the same KEPServerEX instance.
    • Expose the PLC data points as BACnet objects (Analog Input, Binary Output, etc.).
    • KEPServerEX will then act as a BACnet/IP server, allowing Desigo CC to read and write these objects.
  3. Desigo CC Configuration
    • In Desigo CC, add the KEPServerEX as a BACnet device using the same BACnet network settings (Device ID, Port 47808, etc.).
    • Discover or manually map BACnet objects from Kepware.
Keynote:
  • Kepware handles protocol translation internally, so no external BACnet gateway is required.
  • Ensure both systems (Kepware and Desigo CC) are on the same BACnet/IP network segment and that UDP-Port 47808 is open.
  • If your IT policy restricts BACnet broadcast traffic, use a BACnet router or BBMD configuration within Kepware.
You can refer to the official Kepware BACnet/IP Driver Guide and Siemens Ethernet Driver Manual for step-by-step configuration examples. These are available on the PTC/Kepware documentation portal.
Shashi Preetham || +91 8099838801 || shashi@psptechhub.com
pshashipreetham
Keynote:
Tony10264-ParticipantAuthor
Hi Shashi,
Thank you for your reply.
Could you provide more details on how to expose PLC data points as BACnet objects?
Have a nice day.
pshashipreetham
Hi Tony,
Sure, here’s how you can expose PLC data points as BACnet objects in Kepware:
  1. After you’ve created your Siemens PLC channel and device, verify that all the required PLC tags are being read correctly under that device in Kepware.
  2. Create a BACnet/IP driver in the same Kepware project (it can be on the same server instance).
    • Add a new BACnet/IP Channel.
    • Then add a BACnet/IP Device under that channel (this will act as the BACnet server visible to Desigo CC).
  3. Expose the PLC tags to BACnet:
    • Under the BACnet/IP Device, create new tags that reference the Siemens PLC tags.
    • In the Address field, use the full tag reference path from the Siemens device (for example: Channel1.Device1.TagName).
    • Choose the appropriate BACnet Object Type (e.g., Analog Input, Analog Output, Binary Input, Binary Output).
    • Assign Object Instance numbers and descriptive names for clarity in Desigo CC.
  4. Apply and restart the project.
    • The BACnet driver will now publish those PLC tags as BACnet objects that Desigo CC can discover or import manually.
  5. Optional:
    • You can group related tags (for example, temperature, valve states, alarms) by creating multiple BACnet devices for cleaner segmentation.
This approach lets Kepware handle the data translation internally — the PLC tags act as the data source, and BACnet objects are automatically updated and available for BACnet clients like Desigo CC.