How use Kepware to communicate between Siemens PLC and Siemens Desigo CC via BACnet/IP protocol?

  • October 14, 2025
  • 2 replies
  • 558 views

hi guys,

 

Could you know whether Kepware Server can support communication between Siemens PLC and Siemens Desigo CC via BACnet/IP?

 

Although Siemens provides a BACnet gateway for BACnet integration, its network configuration does not comply with IT security requirements. Therefore, I would like to know if Kepware can perform protocol translation. If so, could you provide a configuration manual?

 

Thank you very much.

Best answer by pshashipreetham

Hi,

 

Yes, Kepware (KEPServerEX) can be used to communicate between a Siemens PLC and a Siemens Desigo CC system using BACnet/IP by acting as a protocol gateway.

 

Here’s how it can be set up:

  1. Use the Siemens Ethernet Driver in KEPServerEX to connect to the Siemens PLC (S7-1200, S7-1500, S7-300, etc.).

    • Configure the PLC connection using the proper rack/slot and IP address.

    • Verify data access by browsing the PLC Tags in the Kepware client (Quick Client).

  2. Enable the BACnet/IP Driver in the same KEPServerEX instance.

    • Expose the PLC data points as BACnet objects (Analog Input, Binary Output, etc.).

    • KEPServerEX will then act as a BACnet/IP server, allowing Desigo CC to read and write these objects.

  3. Desigo CC Configuration

    • In Desigo CC, add the KEPServerEX as a BACnet device using the same BACnet network settings (Device ID, Port 47808, etc.).

    • Discover or manually map BACnet objects from Kepware.

Keynote:

  • Kepware handles protocol translation internally, so no external BACnet gateway is required.

  • Ensure both systems (Kepware and Desigo CC) are on the same BACnet/IP network segment and that UDP-Port 47808 is open.

  • If your IT policy restricts BACnet broadcast traffic, use a BACnet router or BBMD configuration within Kepware.

You can refer to the official Kepware BACnet/IP Driver Guide and Siemens Ethernet Driver Manual for step-by-step configuration examples. These are available on the PTC/Kepware documentation portal.

 

Thanks,

2 replies

18-Opal
October 16, 2025

Hi,

 

Yes, Kepware (KEPServerEX) can be used to communicate between a Siemens PLC and a Siemens Desigo CC system using BACnet/IP by acting as a protocol gateway.

 

Here’s how it can be set up:

  1. Use the Siemens Ethernet Driver in KEPServerEX to connect to the Siemens PLC (S7-1200, S7-1500, S7-300, etc.).

    • Configure the PLC connection using the proper rack/slot and IP address.

    • Verify data access by browsing the PLC Tags in the Kepware client (Quick Client).

  2. Enable the BACnet/IP Driver in the same KEPServerEX instance.

    • Expose the PLC data points as BACnet objects (Analog Input, Binary Output, etc.).

    • KEPServerEX will then act as a BACnet/IP server, allowing Desigo CC to read and write these objects.

  3. Desigo CC Configuration

    • In Desigo CC, add the KEPServerEX as a BACnet device using the same BACnet network settings (Device ID, Port 47808, etc.).

    • Discover or manually map BACnet objects from Kepware.

Keynote:

  • Kepware handles protocol translation internally, so no external BACnet gateway is required.

  • Ensure both systems (Kepware and Desigo CC) are on the same BACnet/IP network segment and that UDP-Port 47808 is open.

  • If your IT policy restricts BACnet broadcast traffic, use a BACnet router or BBMD configuration within Kepware.

You can refer to the official Kepware BACnet/IP Driver Guide and Siemens Ethernet Driver Manual for step-by-step configuration examples. These are available on the PTC/Kepware documentation portal.

 

Thanks,

Tony10264-ParticipantAuthor
4-Participant
October 17, 2025

Hi Shashi,

 

Thank you for your reply.

 

Could you provide more details on how to expose PLC data points as BACnet objects?

 

Thank you very much.

Have a nice day.

18-Opal
October 30, 2025

Hi Tony,

Sure, here’s how you can expose PLC data points as BACnet objects in Kepware:

  1. After you’ve created your Siemens PLC channel and device, verify that all the required PLC tags are being read correctly under that device in Kepware.

  2. Create a BACnet/IP driver in the same Kepware project (it can be on the same server instance).

    • Add a new BACnet/IP Channel.

    • Then add a BACnet/IP Device under that channel (this will act as the BACnet server visible to Desigo CC).

  3. Expose the PLC tags to BACnet:

    • Under the BACnet/IP Device, create new tags that reference the Siemens PLC tags.

    • In the Address field, use the full tag reference path from the Siemens device (for example: Channel1.Device1.TagName).

    • Choose the appropriate BACnet Object Type (e.g., Analog Input, Analog Output, Binary Input, Binary Output).

    • Assign Object Instance numbers and descriptive names for clarity in Desigo CC.

  4. Apply and restart the project.

    • The BACnet driver will now publish those PLC tags as BACnet objects that Desigo CC can discover or import manually.

  5. Optional:

    • You can group related tags (for example, temperature, valve states, alarms) by creating multiple BACnet devices for cleaner segmentation.

This approach lets Kepware handle the data translation internally — the PLC tags act as the data source, and BACnet objects are automatically updated and available for BACnet clients like Desigo CC.

Thanks,

12-Amethyst
October 29, 2025

Greetings,

You may visit the link for more info about the BACnet/IP Objects 

https://support.ptc.com/help/kepware/drivers/en/index.html#page/kepware/drivers/BACNET/BACnet_IP_Objects.html

Regards,

Mohit