Kepware compatibility with ControlLogix firmware version
We are using KepServerEX6 (6.6.350.0) communicating to Control Logix PLCs.
We want to upgrade the PLCs to Control Logix Firmware 20.58.
How can I determine if they are compatible?
We are using KepServerEX6 (6.6.350.0) communicating to Control Logix PLCs.
We want to upgrade the PLCs to Control Logix Firmware 20.58.
How can I determine if they are compatible?
Greetings
Please take a look at the following article as it may help resolve your issue:
https://www.ptc.com/en/support/article/CS298912
If you are prompted to log in to view the complete article, you can use your MyKepware login credentials.
I would like to inform you that the Allen-Bradley ControlLogix Ethernet driver cannot communicate with PLC controllers running firmware 20.58 when Protocol Mode in Device Properties | Logix Options is configured as Logical Blocking or Logical Non-Blocking.
I recommend configuring the Protocol Mode to Symbolic under Device Properties | Logix Options, especially after upgrading to firmware version 20.58.
If you have any questions or need further assistance, please feel free to contact us.