Logging DTL with OPC UA

  • February 17, 2026
  • 1 reply
  • 61 views

Hello,
I have a PLC program which send the DTL from the PLC, although I can log the timestamp based on the SQL side, is there anyway to log DTL directly from PLC to Kepware with the new/upcomming updates ?

Best answer by MRohilla

Greetings,

Sounds like Siemens.  DT (Date and Time) is supported, but I believe DTL (Date and Time Long) is still not.  I also believe this is true for Siemens TCP as well as Siemens S7 Plus. The workaround would be to switch the data type in the PLC to DT.

Regards,

Mohit 

1 reply

Support
March 6, 2026

Greetings,

Could you please share the PLC model details with us?

Regards,

Mohit

5-Regular Member
March 6, 2026

I have problem when try to log the DTL data from PLC 1211DC and also 1511PN, both with the newest firmware

MRohillaCommunity ManagerAnswer
Support
March 16, 2026

Greetings,

Sounds like Siemens.  DT (Date and Time) is supported, but I believe DTL (Date and Time Long) is still not.  I also believe this is true for Siemens TCP as well as Siemens S7 Plus. The workaround would be to switch the data type in the PLC to DT.

Regards,

Mohit