Hello,

I'm attempting to add a AutmationDirect CLICK PLC

to our Kepware environment, but not seeing this option for the Automation Direct drivers

 

Anyone ever configure one of these before?

 

Thanks in advance

rajskumarAnswer
16-Pearl
February 6, 2025

Hello, Thank you for contacting us.

It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:

rajskumar_1-1738846893997.png

 


In Kepware, 

  • Right click on Connectivity and Add New Channel of Modbus TCP/IP Ethernet and change name as per requirement
  • Right click on Channel and Add New Device and change name and IP as per requirement(Modbus default port is 502 but you can confirm with device vendor)
    • Refer this article for ID details in Kepware
  • Add tags based on how it is defined in device
    • Refer driver manual for Modbus Addressing here  
    •  
      rajskumar_4-1738846955361.png

       

       

       

       

Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
 
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502

2 replies

rajskumar16-PearlAnswer
16-Pearl
February 6, 2025

Hello, Thank you for contacting us.

It seems it supports the Modbus TCP/IP protocol. To connect this PLC using Modbus TCP/IP to Kepware, you need to follow the steps below:

rajskumar_1-1738846893997.png

 


In Kepware, 

  • Right click on Connectivity and Add New Channel of Modbus TCP/IP Ethernet and change name as per requirement
  • Right click on Channel and Add New Device and change name and IP as per requirement(Modbus default port is 502 but you can confirm with device vendor)
    • Refer this article for ID details in Kepware
  • Add tags based on how it is defined in device
    • Refer driver manual for Modbus Addressing here  
    •  
      rajskumar_4-1738846955361.png

       

       

       

       

Before start , please check if you can Powershell Test-NetConnect to the device on the port KEPServerEX is trying to use.
 
Powershell has a built in commandlet that can help prove or disprove TCP socket connectivity
Command Syntax: Test-NetConnection [host] -Port [port number]
Example: Test-NetConnection 255.255.255.255 -Port 502

Translate
3-Newcomer
February 6, 2025

Awesome, thanks for this info

Translate