How to connect OPCDA - InTouch (HMI) via KepServer EX as an OPC server

  • December 6, 2023
  • 1 reply
  • 3441 views

Hello everyone.

I am an Apps. engineer from South Korea.

I would like to know how to connect OPCDA to InTouch through KepServer EX as an OPC server.

 

We would like to build a connection between our own PC to customer's own HMI (InTouch) to send some data from ours.

Our software has OPCDA Client, so we would like to put KepServer EX into our PC to overcome OPCDA's COM/DCOM barrier.

Once our data is collected in KepServer EX, we would like to send this information to InTouch, so the user can monitor the data through their system.

Is it possible to build connection like the info. above through KepServer EX as an OPC server?

If so, it would be helpful if you could provide us a guide line or manual.

 

Thank you.

Best answer by cmorehead

@KL_10883708 

 

Please take a look at the Kepware knowledge base article in the following link which pertains to remote InTouch connections:

 

Article - CS333066 - Can I Connect to a Remote InTouch Application? (ptc.com)

 

Ultimately, the server must exist on the same machine as an InTouch node. Data from remote InTouch nodes can be accessed via the local InTouch node or with multiple OPC servers using one of the Kepware OPC Client drivers. 

 

Thanks,

*Chris

1 reply

24-Ruby III
December 6, 2023

Take a look - "InTouch: Connecting to Kepware": https://www.youtube.com/watch?v=OVK91uZrC4c

1-Visitor
December 7, 2023

Thank you for your information!
I would like to ask another question related to this.

If I have 'A' PC that has OPCDA & KepServerEx and trying to connect communication with 'B' PC (+HMI (InTouch)),

Does 'A' PC also needs an InTouch component?

If so, then what it could be?

The InTouch program itself or anything else?

cmorehead13-AquamarineAnswer
13-Aquamarine
December 28, 2023

@KL_10883708 

 

Please take a look at the Kepware knowledge base article in the following link which pertains to remote InTouch connections:

 

Article - CS333066 - Can I Connect to a Remote InTouch Application? (ptc.com)

 

Ultimately, the server must exist on the same machine as an InTouch node. Data from remote InTouch nodes can be accessed via the local InTouch node or with multiple OPC servers using one of the Kepware OPC Client drivers. 

 

Thanks,

*Chris