8-Gravel
False alarm triggering and misdata in dababase due to loss of precision of floating-point type data
Dears,
     as screenshoots below, when a simulated float transferred from kepware to thingworx, 1.2 turns to 1.2000000476837158, so a false alarm triggered. Misdata logged in influxdb as well.
  • a simulated float which is 1.2 on kepware
  • but on thingworx that turns to 1.2000000476837158
alarm triggered when property is above 1.2
  • So a false alarm triggered
I can't change data restricted to external audit, what can I do to modify the data to the correct.
Rocko
Have you made sure that the value on Kepware really is 1.2 and not 1.2000000476837158 just being displayed as 1.2 in the Quick Client?
LeoChen8-GravelAuthor
8-Gravel
check property in qc, it is 1.2
Or try to write 1.2 to this remote tag on thingworx, value also turns to 1.2000000476837158
  • write 1.2 to the tag
     Then value turns to 1.2000000476837158
 floate points has the question.
Rocko
This is actually expected behaviour and a consequence of using float type in Kepware instead of double.
Check this article for reference: https://www.ptc.com/en/support/article/CS341193
https://www.h-schmidt.net/FloatConverter/IEEE754.html
To work around this, use double in Kepware or transform your variable in TWX with toFixed.
Support
Hi @LeoChen ,
It appears that the previous reply by Rocko answers your question.  For the benefit of other Community Members who may have the same question, it would be great if you could designate it as the Accepted Solution.
In the event that this response did not answer your question, please post your current status so that we can continue to support.
Thanks for using the PTC Community!
Tony