As per the original post.

 

Hi,

 

I have the similar problem as NM_12850686. Could you please share the port issue solution?

 

Here is my setup:

Cleco Controller mPro200 - Open Protocol - Port 9002 - Activated

Cleco Controller mPro200 - TorqueNet- Port 12345 - Activated

Cleco Controller mPro200 id : 192.168.50.20

20250425_181652.jpg

KepServerEx - Channel:TorqueToolEthernet - Device:Cleco (Open Protocol - 192.168.50.20 - Port: 9002)

LP_12507955_0-1745595100244.png

 

Both the controller and the port can be ping successfully from the PC.

LP_12507955_2-1745595271190.png

 

However, none of the tags receives information from Cleco. Could you please look into this?

LP_12507955_1-1745595205950.png

 

Thank you,
LP

MKhatriAnswer
Support
Jun 22, 2026 4:54 PM UTC

Greetings LP_12507955 ,
 

  • Connectivity to port 9002 is OK (Test-NetConnection success ✅), so network is not the issue.

  • From logs (image), Kepware shows “device not responding / timeout / write rejected / bad quality” → indicates protocol-level issue, not port issue.

  • Possible causes:

    • Open Protocol not fully enabled/configured on Cleco controller (MID messages not active)
    • Kepware driver expects specific Open Protocol handshake (MID 0001/0002)
    • Controller may require login/acknowledgment before sending data
    • Wrong controller mode (tightening vs monitor mode)
  • Checks to perform:

    • Verify Open Protocol license/activation on mPro200
    • Confirm MID traffic via Wireshark (data actually coming or not)
    • Ensure correct device model/driver mapping in Kepware (Cleco Open Protocol driver)
    • Check if controller requires KeepAlive/heartbeat
  • Important:

    • Ping/port open ≠ data communication working
    • Issue is application/protocol layer, not network
  • Suggestion:

    • Enable detailed diagnostics in Kepware
    • Cross-check using third‑party Open Protocol client tool to validate controller response

6 replies

pshashipreetham
19-Tanzanite
May 2, 2025 5:50 PM UTC

Hi @LP_12507955 

 

My Observations are 

Network connectivity is not the issue

  • Your Test-NetConnection result shows port 9002 is reachable.

  • Device IP is correct.

  • Controller port is activated, and protocol is set to Open Protocol.

No MID 001 Communication happening

From your Kepware logs and screenshots:

  • Kepware is not receiving responses from Cleco (timeouts or blank reads).

  • Likely causes:

    • Incorrect MID polling config

    • Missing handshake

    • Wrong Job selection, or missing Start request MID

    • Cleco not configured to auto-transmit data

 

Solutions May be:

1. Controller-Side Validation

  • On the Cleco mPro200, go to:

    • Menu > Protocol Settings > Open Protocol > Advanced

    • Ensure MID 001, 005, 006, 0062, 0064 are activated for replies

    • Set Primary Trace MID = 0064 or the expected MID your system should respond with

    • Enable Auto-send MID 0064 on job completion

Also check:

  • "Controller Auto Start Job" is enabled

  • Job ID is pre-assigned or ready to be started from OPC (Kepware)

Why this matters: If the controller is waiting for a MID 003 (Job Select) or MID 001 handshake, and it's not received, it won't push out MID 0064 (tightening results).

 

2. Kepware Device Settings

From your screenshot:

  • Job Select Method: Try setting it to None initially for testing

  • Start MID: Enable “Send MID 003” to select Job

  • Enable Auto-send MID 0064 (result transmission from Cleco to Kepware)

Also:

  • Increase Timeout from 5000 ms to 10000 ms for slow reply testing

  • Ensure Device Read Mode is set to either On Demand or Cyclic (not “None”)

 

3. Trigger Initial MID

Kepware won’t automatically initiate MID 001 unless the driver does so or tags are manually activated.

To verify:

  1. Go to Quick Client

  2. Right-click any writable command tag (like MID_003_JobNumber) and write a valid job number

  3. Then write 1 to the Send_Job tag (or equivalent) to send MID 003

  4. Observe if Cleco replies with MID 006 or MID 0064

If this works, the issue is that the controller needs an explicit MID trigger to start sending.

 

Use UaExpert to Compare

If the MES is not reading but UaExpert is:

  • Use UaExpert to create a monitored item on tag like Torque or ResultID

  • Perform a real tightening operation on Cleco

  • See if MID 0064 values populate

If UaExpert sees values but Kepware does not:

  • Likely a job trigger/start MID missing from Kepware

  • Or MES needs to send command MID to initiate data

5. Firmware or Protocol Mismatch

Check:

  • Cleco firmware matches the Open Protocol version expected by Kepware

  • If Cleco uses a custom MID map, the default OPC tag structure in Kepware may not match

Use Cleco’s documentation to verify which MIDs are enabled and what data formats are used.

 

Thanks,

Translate
Shashi Preetham || +91 8099838801 || shashi@psptechhub.com
3-Newcomer
May 9, 2025 5:47 PM UTC

Things I learned - you can't read tool_enable only write it. 

You need to add every tool in kepserver.

They will have the same IP address as the controller but the port that is mapped to them in the controller.

You will need to address the tool  as toolname.tagname  when controlling remotely. I used ignition and OPC

Easiest thing to get working is reading the CommChanelId - should match the toolgrp in the cleco controller.

Also you can send TimeSync and read back time.

If you get those working through quick client, you're good. 

 

 

I found Cleco MPRO  was best controlled via app numbers.  I am using no MIDs directly. 

I am sending enables, app numbers, and reading back LTRs. All those are available in the tag library when you add a new tag. 

I mostly got tripped up on needing to use app numbers and on needing to use the tag library in KepServer.  When I tried to use MIDs to start communication for example, that was built into kepserver. If you let the tool do the work, it is easier.

Translate
1-Visitor
Mar 19, 2026 5:53 AM UTC

Hi, may I know if there are any updates or results available? Kindly let me know, Im also facing same situation your help will be valuable.

Translate
5-Regular Member
Aug 7, 2026 12:35 PM UTC

Answers here does not work for me. They all defniately feels like AI-written. I walked around by controlling the Cleco indirectly - via the robot controller. So it will be like: Cleco → robot (controller) → PC with KepServerEx. Instead of Cleco → PC with KepServerEx. I contacted KepServerEx support directly, have a teamview session, and it didn’t work as well. 

Translate
MKhatriCommunity ManagerAnswer
Support
Jun 22, 2026 4:54 PM UTC

Greetings LP_12507955 ,
 

  • Connectivity to port 9002 is OK (Test-NetConnection success ✅), so network is not the issue.

  • From logs (image), Kepware shows “device not responding / timeout / write rejected / bad quality” → indicates protocol-level issue, not port issue.

  • Possible causes:

    • Open Protocol not fully enabled/configured on Cleco controller (MID messages not active)
    • Kepware driver expects specific Open Protocol handshake (MID 0001/0002)
    • Controller may require login/acknowledgment before sending data
    • Wrong controller mode (tightening vs monitor mode)
  • Checks to perform:

    • Verify Open Protocol license/activation on mPro200
    • Confirm MID traffic via Wireshark (data actually coming or not)
    • Ensure correct device model/driver mapping in Kepware (Cleco Open Protocol driver)
    • Check if controller requires KeepAlive/heartbeat
  • Important:

    • Ping/port open ≠ data communication working
    • Issue is application/protocol layer, not network
  • Suggestion:

    • Enable detailed diagnostics in Kepware
    • Cross-check using third‑party Open Protocol client tool to validate controller response